residential garage

Status
Not open for further replies.

vinster888

Senior Member
what we do is run nm cable and protect it up to 8' or ceiling. whichever is greater. typically a 4 square box with an r/s cover and 3/4" PVC up. save the customer a couple bones and doesn't look as bad when you run the wires in a workperson-like manner
 

M. D.

Senior Member
Thankfully in Mass we have this exception,.. Perhaps someday the NEC will adopt similar language

Exception No. 2 to (3): For detached buildings that are accessory structures to dwelling
occupancies, Type NM, Type NMC, and Type NMS cables shall be permitted to be used without
concealment.
 