When determining the correct kva to insert on each phase of a panel schedule for a three phase load should the total KW be inserted at each phase or is the total divided by 3 and then inserted on each line? In other words if an HVAC unit is a 5KW load at 208v three phase is 5000 inserted on each line or is 5000 divided by 3 (1666) and then inserted? Of course I guess the PF would need to be figured to convert from KW to KVA at probably .80
And on the same line would a motor load be converted to kva from table 430.250 as the FLA x 120v for each phase? Or would the FLA be multiplied by 208v, then divided by three.
I would appreciate any thoughts on the correct methods!