io748
- Nashville, NC
My facility has 9 double ended substations (M-T-M) that have kirk key interlocks. When our facility was constructed it was fed from two substation transformers, whose primaries were connected to the same feed from the utility. Some time later one of the transformers was removed, and both main feeds into the plant were connected to the same source.
Question 1: It has been suggested to me that the kirk key system could be bypassed safely, since both sides of each substation are fed from the same source. This is desirable as I could test the main breakers and switches with no outages. Does anyone see any issues with bypassing the kirk key system, given this situation?
Question 2: Each main breaker is 4000A, and the tie breaker is 4000A. The feeder breakers on one side total 4000A. So if you have the tie breaker closed and one main open, 8000A of breakers will be fed from one 4000A main. Why would the founding fathers of this plant have not double sized the main breakers?
As an ex-controls guy who is just starting a new role as a facilities electrical engineer, any input is appreciated.