Have 3 - 150HP motors with 3 - 200amp disconnect switches feeding each .Nameplate amps are 167 amps .By code a 400amp switch should have been used ( 430.110 - "1.15 x 180 = 207 amps " ).What shall I tell my boss the reason we have to upgrade to 400 amp switchs ? I know about risk of opening under load ,any other risks involved to justify expense ??? No vfd involved these are across the line starters .These have 200 amp time/delay Rk1 fuses and have had no problems starting ?