Conductors of different voltages, panels in same raceway

Status
Not open for further replies.

Lancito

Member
I was recently on a job where per drawing both 120v and 277v conductors were installed in the same conduit. Is legal per art. 300.3 (C) (1) of NEC or not?
 

480sparky

Senior Member
Location
Iowegia
As long as both are rated for the higher voltage, you're OK. Most building wire is rated 600v anyway, so you're covered.
 