peter d

Senior Member
Location
New England
Many local codes are more stringent than the NEC with regard to fire alarm wiring. In my area, all fire alarm wiring has to be in metal raceway and/or MC cable.

Only your local authority can answer this question.
 

DM2-Inc

Senior Member
Location
Houston, Texas
Also consider what the system is being used for. If the system is being used for a Fire Suppression system in accordance with NFPA 2001 (2008 edition, and earlier), section 4.3 makes the following statements:

4.3.1.1 Detection, actuation, alarm, and control systems shall be installed, tested, and maintained in accordance with appropriate NFPA protective signaling systems standards. (See NFPA 70 and NFPA 72. In Canada refer to ULC S524-M91 and ULC S529-M87.)

4.3.1.3 Initiating and releasing circuits shall be installed in raceways. Other than as permitted in 4.3.1.3.1, alternating current (ac) and direct current (dc) wiring shall not be combined in a common conduit or raceway.

4.3.1.3.1 Ac and dc wiring shall be permitted to be combined in a common conduit or raceway where shielded and grounded.​
 