Two questions.

Status
Not open for further replies.

Goofy5953

New member
Lights that are controlled by a light switch. Continuous or non-continuous load? I say non. For info they are in a large residential barn/garage w/high traffic. I know location doesn't matter, just trying to give info.

Also 20 amp light circuit. 15 amp switches. Load is less than 10 amps. Code says not in nut shell not to overload switch.

Looking for specific articles to help my case. Thanks....
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
I don't believe the fact that a switch is involved would determine the use as continuous or not. If the lights are likely to be on for more than 3 hours than I would say continuous.

The switch being 15 amp is fine as long as the load on the switch does not go over 15 amps.
 

steve066

Senior Member
In my opinion, any lighting branch circuit is continuous.

I have always assumed a the rating on a light switch was based on continuous load, and a 15 amp light switch could be loaded to 15 amps forever. Is that incorrect???
 

wasasparky

Senior Member
Thanks
But I still need 20A wire on both sides of that 15A switch...:roll::roll::roll:

I keep thinking about the people who wire only 20A residential circuits.
Some thought OK to use #14 to the light, as there is very little load...they were set straight...

If a reduction in switch ampacity is allowed, why not the conductor?
(Just being devil's advocate here - don't flame me:smile:)
 

benaround

Senior Member
Location
Arizona
I keep thinking about the people who wire only 20A residential circuits.
Some thought OK to use #14 to the light, as there is very little load...they were set straight...

If a reduction in switch ampacity is allowed, why not the conductor?
(Just being devil's advocate here - don't flame me:smile:)

What size conductor would you use with a 600w dimmer on a 20a branch circuit.

600/120 = 5a
 