Care to explain what this means?
Sure. Aboard ship, we use a floating ground system, since it's illegal, vice the CFR 111.05-11, to use the ship's hull as a conductor,(except for certain limited circumstances).
Since I am, essentially, the Chief Cook and Bottlewasher of my very own utility company, from the generators,(4 auto-paralleling 6.6 kv turbo-diesels), right down to the light bulbs, I get to look at the entire picture.
Out here, deliberately "grounding",(actually "hulling"), one of your legs is also incredibly wasteful, not to mention destructive to things like intended sacrificial anodes and unintended anodes, (like where the different steels of bearings meet the mild steel of the hull, and welded seams of the plates,all immersed in seawater...BAD!).
On my installation, I have Bender Ground Detectors tied into the central engine alarm system, and am installing Erickson Ground Deteclor Lights at the Distribution panels,(it will ease my task of "chasing grounds"...plus, I'm a bit "old school"...I've sailed a lot of ships built in the 1960's, where every distribution and feeder panel had GD lights standard).
If I were to ground one of my phases, the Chief Engineer and the bean counters at World Headquarters would initially get all squiffy about the ship's increased fuel consumption figures. And then would flip right out at the next shipyard period from all the "change orders".
But even shoreside, if you think about it, the customer is paying for the current on all 3 phases, so to then take one of those phases and send it back through the earth to the opposite pole of the generator without it doing much, (if any), useful work...
I s'pose there are very good reasons for this, but it seems odd from where I float.