Old wiring in attic and crawl space

Status
Not open for further replies.

raider1

Senior Member
Staff member
Location
Logan, Utah
There is no NEC requirement that abandonded wiring other than limited energy type of wiring (Phone, class 2 &3 etc..) be removed.

Chris
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
Does it have to be removed if it's not being used? Thank you.
If you are talking about NM cable then, No but I have heard some inspectors make others terminate it in a JB. If it is not connected at either end then it has nothing to do with us. I do try and remove what I can but it is not necessary.
 

SEO

Senior Member
Location
Michigan
I only see the cables listed in sec 820.25 and 830.25 that would have to be removed or identified for future use. Could be a local rule.
 

raider1

Senior Member
Staff member
Location
Logan, Utah
I only see the cables listed in sec 820.25 and 830.25 that would have to be removed or identified for future use. Could be a local rule.

For other sections for abandoned wiring from the 2008 also take a look at 640.6(C), 645.5(F), 725.25, 760.25, 770.25, 770.154, 800.25, 800.154.

Chris
 