What is the lowest power factor that a motor can have when unloaded or lightly loaded. I have a 480V 3P 150hp motor which is lightly loaded and when measuring with a power meter I see a power factor of .179. This power factor seems extremely low. I know that a lightly loaded motor will have a low power factor, but this value seems very low. Does this power factor of .175 seem too low?
The full load power factor for this motor is about .80. I have double checked power meter connections and everything seems correct. We are running about 50A when measuring and according to datasheet this 50A corrosponds to about 1/4 loading on the motor. For 1/4 loading on the motor the datasheet lists a power factor of about .60. So I'm wondering if I am doing something wrong in my measurments or can a motor really have such a lower power factor?
The full load power factor for this motor is about .80. I have double checked power meter connections and everything seems correct. We are running about 50A when measuring and according to datasheet this 50A corrosponds to about 1/4 loading on the motor. For 1/4 loading on the motor the datasheet lists a power factor of about .60. So I'm wondering if I am doing something wrong in my measurments or can a motor really have such a lower power factor?