jwelectric
- North Carolina
And it doesn't say it can't.
Since this section is addressing only the electrode, it has absolutely nothing to say about the aboveground rebar, correct? Nowhere does it say you cannot use tie-wire aboveground?
Since tie-wire is the standard industry method of connecting rebar together, why would we assume, and yes, I said assume, that the tie-wire cannot be used on the rebar which is not in the slab? Where is it prohibited?
If it isn't specifically prohibited, wouldn't the industry standard method apply?
Now, if you look hard, yuo can probably find something in 110 to bust me with.:wink:
I don?t know the building codes which regulate the installation of reinforcing bars installed in footers but I am sure that there is a lap distance for a rebar that is tied together and the building codes also regulate the exposed portion of rebar also and I don?t think that exposed reinforcing steel is allowed except where another pour is coming at a latter date and then the building codes requires that the rebar be protected from corrosion during the time it is exposed.
At the present time the only electrode that we are allowed to connect a grounding electrode conductor or bonding conductor to exposed metal is building steel and permission has been given to use the first five feet of interior metal water pipe.
The practice of hitting an exposed piece of rebar is not allowed under today?s NEC.
250.64(F) states that the grounding electrode conductor and/or bonding jumper MUST hit the electrode or a busbar not less than ? by 2 inches.
Nowhere in the 2008 code does it allow hitting an exposed piece of rebar in any manner. The conductor must hit the electrode and the only part of the reinforcing steel that is electrode is that part that is encased by no less than 2 inches of concrete as outlined in 250.52(A)(3).
Therefore unless the conductor is terminated on the inside of the concrete then it is not being terminated on the electrode and is a violation of the NEC.
When I hear someone come out with the comment that the code don?t say I can?t so that means that I can, I can?t help but to think that the code doesn?t say that I am not allowed to relieve myself in an energized disconnect either so using the above statement I suppose that I can. Be back in a few minutes as I have already had several cups of coffee this morning and need some relief and my service is energized.
?.A few minutes goes by??
?.A few more minutes goes by??
?.Mike, Mike, Mike where are you???...
Well the code didn?t say he couldn?t so I guess he did. This story shall continue when all the arrangements have been completed. :grin::grin::grin: