sevlander
Member
- Location
- new jersey
Can someone tell me if there is any other way to calculate voltage drop for lighting other than 3% for branch circuit and 5% for BC and feeder combined? We are involved in the design of a building renovation in which existing 100 watt MH soffit recessed fixtures are to be fed and added to. The building is approximately 300' long with around 60 fixtures. We are calculating # 8 wire and larger depending on circuit wattage and length. The contractor contests that the existing lights work fine with #12 wire and that as long as the VD is less than the manufacturer's minimum voltage requirements it is fine. I don't know of any allowance of this kind in the NEC, am I correct? Thanks, Scott