Are the owners going to rewire the house? I cannot answer that question, I am not in control of the job.
Note:
The homeowners were on vacation when this happened. When they got home, the street repairs by the utility company and the tree removal (actually 3 very large trees) was complete.
The utility company turned the power back on to all of the houses (not many in this area, but the primary came down, so who knows how many houses were affected), and the homeowners had power on until the day I was there for the testing. I told them not to restore power after my testing until the corrections were effected, but I have not authority on this job, I am just a consultant for the EC.
I would take an educated guess that 75% of the house was recently updated with wiring and a new service (2 years ago).
I did not megger the panel, I meggered the branch circuits and the SER/SE service cables. I used the Fluke model 1587.
I meggered hot-grd; hot-hot; hot-neutral.
I checked (as I always do) to see that the contractor did not miss disconnecting any of the loads. He missed a couple of lamps in hihats and then we started.
Someone mentioned that the SER in the panel did not fault, but the cable next to it. That is correct, the SER was scorched, yet not damaged.
I am tending to agree that the utility fault came in on the grounded/neutral conductor went through some loads, and found a way back out through the grounding electrode system.
Why some circuits are not affected always baffles me. Someone mentioned the circuits affected may be the ones with larger loads...that is an interesting concept.
Thanks for all of the help!!!