chevyx92
Senior Member
- Location
- VA BCH, VA
Inspector 404.3(B) and says we can not have a nipple between our two section panelboards. I gave him a call and cited 312.8 and said I feel it's ok. He then tells me that section is for Cabinets, Cutout Boxes and Meter Socket Enclosures. He said that panelboards don't fall under this section. I argued that a panelboard meets the definition of a "Cabinet". He then saw my point and agreed that a panelboard would fall in this category. He said he would allow the nipple if I comply with 1 of 2 conditions. Either provide him with literature from the panelboard manufacturer stating its ok to use that panel for a raceway or give him a calculation showing I'm not over my fill in the panel. Does anybody else think he's going a bit far with his interpretation and conditions? This was the chief electrical inspector I spoke to.