Does anyone know how I can protect a Steel City 4 x4 box (which is good for up to two hours) in a 3-Hour rated wall?
Can you prefab a sheetrock box around the 4" square box?Does anyone know how I can protect a Steel City 4 x4 box (which is good for up to two hours) in a 3-Hour rated wall?
If the op already has a 2 hour rating on the walls wouldn't the putty add the extra hour needed?
2 pieces of sheetrock double the fire ratingNot unless there is a tested assembly using the putty pad to acheive a 3 hour rating.
The problem is that with fire rating you can't just take 2- 1 hour rated pieces of equipment and add them together and get a 2 hour rating. Each rating must be done with a tested assembly.
A standard 4 square metal box without a putty pad is premitted to be used in up to a 2 hour rated assembly provided that they meet the requirements of Exception #1 to 712.3.2 of the IBC.
Chris
2 pieces of sheetrock double the fire rating
I see, and I am assuming the Fire Putty Pad company doesnt goto that extent. That why its only good for an hour?