A UPS rated at 14 KW but loaded to only about 3.5 KW certainly wont normaly draw 14 KW from the supply, where would all this power go ?
It certainly wont produce over 10KW of heat !
Under normal operating conditions, I would expect it to draw about 4 or 5 kw. Exact figures can only be obtained by accurate measurement or enquiry of the manufacturer.
Care must however be taken when sizing wire and breakers for large but lightly loaded UPS units.
Remember that following an outage, the UPS will draw extra power from the line in order to charge the internal batteries.
This extra load can be greater than expected in the case of large but lightly loaded UPS units.
As a rough "rule of thumb", in the absence of detailed instructions, circuits supplying fully loaded UPS units should be sized at 150% of the rated output, to allow for losses, and for charging the battery after an outage.
Therefore for a 3.5KW UPS, the branch circuit should be able to supply about 5.3 KW.
For a 14 KW UPS , the branch circuit should be able to supply about 21 KW.
Now consider a 14KW UPS but only loaded to about 3.5 KW as in the O/P.
Although in normal use, it will only draw about 4/5 KW this does NOT mean that a branch circuit designed for 4/5 KW will suffice.
Following an outage, the UPS will require up to 7KW (50 % of its rating) to charge the battery, AND 4/5KW to supply the load.
Therefore a branch circuit suitable for about 11/12 KW will be required.
Quite a difference between a fully loaded 3.5KW UPS and a 14 KW one loaded to only 3.5 KW !
The input wattage under normal conditions of a 3.5 KW UPS and a 14 KW UPS loaded to only 3.5 KW, will probably be broadly similar.
However the bigger unit will require a much larger circuit ampacity on account of the extra battery charging demand following an outage.