Does the light canopy count for box fill ?

Status
Not open for further replies.

glene77is

Senior Member
Location
Memphis, TN
Well it passed, the inspector never said a thing about the pancake boxes. We had 14-3 in every one of them.

But they do get good retirement benifits.

Buck,
The 14-3 must have been to a Fan/light?

I worked 20 years at the State for my pension,
and made more money than I do now,
and "Yes" that benefit really helps nowadays,
while I wait for spring-:)time and the economy.
 

hillbilly

Senior Member
IMO 410.20 doesn't apply.

Article 410 (2005) (420 2008?)
Section III. Provisions at Luminaire (Fixture) Outlet Boxes, Canopies, and Pans.

410.10 Space for Conductors.
Canopies and outlet boxes taken together shall provide adequate space so that luminarie (fixture) conductors and their connecting devices can be properly installed.

How does that not apply?
It says what it says.:roll:

steve
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Article 410 (2005) (420 2008?)
Section III. Provisions at Luminaire (Fixture) Outlet Boxes, Canopies, and Pans.

410.10 Space for Conductors.
Canopies and outlet boxes taken together shall provide adequate space so that luminarie (fixture) conductors and their connecting devices can be properly installed.

How does that not apply?
It says what it says.:roll:

steve

It says what it says but what does it mean? It says that they shall provide adequate space whatever that means? How do you calculate adequate space? :confused:
 

radiopet

Senior Member
Location
Spotsylvania, VA
I have a hard time enforcing "adequate space" versus exactly what it says in 314.16(A). Is it to be implied that 410.20 is the common sense approach to what 314.16(A) actually says. I doubt it.
 

480sparky

Senior Member
Location
Iowegia
I'm surprised the word 'adequate' is still in there. The word is listed in T3.2.1 of the NEC Style Manual as a term that is possibly vague and unenforceable.
 