Does a stand by generator with a service rated breaker, mounted on the unit, also need a disconnect before it enters a building ?
Does a stand by generator with a service rated breaker, mounted on the unit, also need a disconnect before it enters a building ?
702.11 States that the disconnecting means must be suitable for use as SERVICE EQUIPMENT. Which, I think, means that you need an enclosure that is service rated. Anyone else see it this way?:-?Check out 702.11
and the definition of readily accessible
The article your looking for is 702.11.Does a stand by generator with a service rated breaker, mounted on the unit, also need a disconnect before it enters a building ?
702.11 States that the disconnecting means must be suitable for use as SERVICE EQUIPMENT. Which, I think, means that you need an enclosure that is service rated. Anyone else see it this way?:-?
Does a stand by generator with a service rated breaker, mounted on the unit, also need a disconnect before it enters a building ?