ptonsparky
Tom
- Occupation
- EC - retired
We connected 8KW diesel generators in a trailer for insulators. Set up a small panel with CBs and the whole thing. Units worked great but were a little small when the temp went down and the connected equipment was harder to start. These sets were hardwired to a panel and we bonded the neutral to the frame of the trailer. No rods required.
The customer bought two 15KW gas Generac units to replace the 8s and set them in the back of crew cab pickups. The units have recepts on the gen. OK. Just install a 4wire 50 amp cord to my trailer mounted panel/equipment and be done. The guys checked operation of GFCIs both on the gen and in the trailer. The "test" buttons trip the GFCI but a Fluke T Pro will not. We bonded the gen frames to the bed of the truck. The neutral of the gens float. How are these GFCIs going to function? As I see it they will not operate on the first ground fault but will on a subsequent. Not sure what will happen if/when the first fault is L1 and the second is L2.
The customer bought two 15KW gas Generac units to replace the 8s and set them in the back of crew cab pickups. The units have recepts on the gen. OK. Just install a 4wire 50 amp cord to my trailer mounted panel/equipment and be done. The guys checked operation of GFCIs both on the gen and in the trailer. The "test" buttons trip the GFCI but a Fluke T Pro will not. We bonded the gen frames to the bed of the truck. The neutral of the gens float. How are these GFCIs going to function? As I see it they will not operate on the first ground fault but will on a subsequent. Not sure what will happen if/when the first fault is L1 and the second is L2.