The following was sent to me via PM so I am posting it here in a thread of it's own for discussion.
How are
Please explain and give me the answer following questions because this is very important for my work thank you very much (for non dwelling units)
1-Is this A/C (air conditions) loads continuous or non continuous loads?
2- Is electric space heating loads continuous or non continuous loads?
3- Is motors load continuous or non continuous loads?
4-if I make design of motor control center panel for air conditions loads and motors and delta/star starting is this needs to apply 440.22(b)(1) and 430.52 table for selecting over current protection device or the code have another solution for this case
4-if I have panel board contain 3 lighting circuits, 4 receptacles circuits, 6 A/C (air condition) circuits if I want to size the circuit breaker of panel and the conductor what is the suitable section for this
a-use 210.20 for circuit breaker sizing and 210.19 for for main conductor sizing
Or use
b-440.22(B)(1) for circuit breaker sizing and 430.34 for for main conductor sizing
Thanks
Roger
How are
Please explain and give me the answer following questions because this is very important for my work thank you very much (for non dwelling units)
1-Is this A/C (air conditions) loads continuous or non continuous loads?
2- Is electric space heating loads continuous or non continuous loads?
3- Is motors load continuous or non continuous loads?
4-if I make design of motor control center panel for air conditions loads and motors and delta/star starting is this needs to apply 440.22(b)(1) and 430.52 table for selecting over current protection device or the code have another solution for this case
4-if I have panel board contain 3 lighting circuits, 4 receptacles circuits, 6 A/C (air condition) circuits if I want to size the circuit breaker of panel and the conductor what is the suitable section for this
a-use 210.20 for circuit breaker sizing and 210.19 for for main conductor sizing
Or use
b-440.22(B)(1) for circuit breaker sizing and 430.34 for for main conductor sizing
Thanks
Roger