Feedback on voltage drop situation

Status
Not open for further replies.

sw_ross

Senior Member
Location
NoDak
I'd like some feedback on an install I'm working on.

I'm running a 120v circuit out to a 4/10 hp lift pump in a septic tank. It's about 240-250 feet from the panel to the tank. I did a voltage drop calc. and came up with about 8 volts of drop, or 6.7% (FLC from NEC 430 charts).

When I brought this up to my boss and asked if he wants to up the wire size, he acted surprised that I was concerned about the issue. He has more experience with this sort of thing than I do. I know what the books say, but in real world situations am I overly concerned about this?

Thanks,
Sky
 

mcclary's electrical

Senior Member
Location
VA
What size wire did you use for a calculation? We're only talking about 311 watts. 311 watts is a small load. Unless you're using speaker wire, you should be fine:grin:
 

sw_ross

Senior Member
Location
NoDak
Wouldn't a 4/10 hp motor at 120v be around 8 amps FLC? (from 430.248)

P.S.- Thanks for the feedbacks so far!
Sky
 
Last edited:

winnie

Senior Member
Location
Springfield, MA, USA
Occupation
Electric motor research
IMHO for this application, the key voltage drop issue won't while the motor is running, but instead the voltage drop while the motor is starting.