I was looking at the breaker schematic for a 5kV breaker the other day when I came across something odd it the control circuit. The trip coil of the breaker (52T) has a Red indication light "R" in series with this trip coil.
The part that I found strange was the fact that the red light was lit when the breaker was in operation. Looking at this red light in the circuit at first I thought that since this light was in series with the trip coil the light would be lit but also cause the trip coil to trip the breaker (Breaker is tripped only by switch or overload contact)
After thinking about it I noticed what looks like a resistor in series with the light. I then though that maybe the light and resistor combination had a much higher impedance than the trip coil and therefore the majority of the voltage appears across the resistor and light and very little across the trip coil thus causing it not to operate. The voltage across the light in this combination is enough to power the light however.
When the switch or overload contacts close, the full voltage is seen across the trip coil and thus it will operate.
Am I right with my thinking in regards to the higher impedance of the light causing the trip coil not to trip?