In service MV cables should not be DC hipotted per ICEA, ANSI, IEEE, or NETA standards, it is considered a destructive test and may damage the cable, or at least reduce the life. PF, TD, VLF, or PD testing should be done on service aged MV cables.
As Brain said, you would always megger prior to doing an overpotential test.
There are no "good readings" when hipotting, it is all about the trends when done properly.
If you need to ask these questions, you should not be testing MV cables or transformers, call a specialist who does this for a living.