woodduder
Senior Member
- Location
- West Central FL.
Long day with the AHCA inspection team. All went well except for one item and I didn't bring a code book home. In all of our tranformers we installed 3 single lugs which we drilled into the side of the transformer housing, ground away the painted surface and 1/4 x 20 bolted each lug seperatly. The inspector is telling us that this is not acceptable and that we must "per the NEC....bond all these lugs together" even though they are all 1/2" away from each other on the same metal surface. Assuming we have lugs rated for two conductors, he wants me to link them together or obtain a lug/bar so they will all be together. I always thought and have always installed seperate lugs with no problems ever. What do you guys think?