I have a 400 amp 480v service .From pole to ct is 60 feet. Would you guys run 1 set of 600 mcm or two sets of 4/0. There is only 1- 4" pvc
Depending on 3 wire or 4 wire service you would need to derate the 4/0's to 80% or 70%
neither add up to 400amps.
I have a 400 amp 480v service .
What am I missing. 4/0 THHN/THWN-2 260 x .8 = 208 x 2 = 416
but what about 310.15(b)(2)(c) ? Not a factor ?
What am I missing. 4/0 THHN/THWN-2 260 x .8 = 208 x 2 = 416
It was and I could have explained myself better when I said I needed 400 amps.
I started with 100 F and went with the 40 F adder. along with the double 125% that PV systems require, I can not remember what the 'real' load was but it was not very high at all.
As long as the load calc showed a load of 364 amps or less, you would still be ok.Sorry Gus I was using the 75deg column, but, to save face just a little if it was a 4 wire
system @ 70% derating = 364amps.
Frank, not challenging you, and you are correct, curious, how often have you seen a service with a major portion of the load nonlinear ?
That's not intended to be "smart alec", but I often wonder. I don't recall ever seeing one.
It was and I could have explained myself better when I said I needed 400 amps.
I started with 100 F and went with the 40 F adder. along with the double 125% that PV systems require, I can not remember what the 'real' load was but it was not very high at all.
I'm surprised no one has mentioned one set of 500's. What is the calculated load? BTW that is what I would pull.