Practical limit conductors in motor J Box

Status
Not open for further replies.
Does any one know of a table listing the practical limit on conductor sizes in various 480 volt 3 ph motor Junction Boxes. Above 250 HP I will go to medium voltage with fabricated J Boxes.
Ray Ploeger P.E.
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
In theory the supplied motor junction box is suitable for conductors sized per the rules in Article 430.
 

jdsmith

Senior Member
Location
Ohio
For NEMA 1 to NEMA 3 starters we often pull conductors that are suitable for the largest motor that could be connected to the starter, aiming for a maximum voltage drop of 3% on the motor feeder. Typical distance from an MCC to a motor are on the order of 400-800 feet in the refinery so cables are usually upsized one or two sizes beyond the minimum for a given motor. We use all IEEE 841 motors with oversized motor makeup boxes and have not had a problem fitting the terminations in the box.

This doesn't exactly answer your question, but you could compare the junction box sizes in IEEE 841 with the sizes in NEMA MG-1 and then look at feeder cable sizes to get some idea. We have a project to refeed 200 or so motors over the next year and a half so I'll try to take notes as we move along - this would be a good table to have for reference.
 