powersurge781
Member
Am pulling 3 400mcm and 1 2/0 ground thhn in one 4" conduit, with a total of 3 conduits (with 4 conductors) over 320' for a 1000A /1ph/240v panel. Would like to use only one pull box (N48) in the middle to try and eliminate any junctions. I know this will require me to pull extra wire through the box or start in the middle and pull off the rest to refeed back into conduit and to the end. Any suggestions? Would hate for a junction to go bad... under 10' of snow.