acwservices
Senior Member
- Location
- Eastern NC
I'm a little confused over 210.12 of the 2008 NEC. It specifically states "All 120-volt, single phase, 15 and 20 amp branch circuits.....shall be protected by a listed arc-fault circuit interrupter." There are two exceptions, but neither address if the circuit is already protected by a GFCI. My question is- are the circuits that require GFCI protection, such as the kitchen sabc, required to also have AFCI protection? I thought they were since 210.12 states ALL, however on page 39 of Mike Holts book titled "Changes to the NEC 2008," MH states that "the 2008 NEC requirement does not require AFCI protection in rooms or areas where GFCI protection of receptacle outlets is required."