What is the maximum height that you can place a receptacle in a family room and still meet code requirement?
Thanks,
Thanks,
210.52 Dwelling Unit Receptacle Outlets.
This section provides requirements for 125-volt, 15- and 20-ampere receptacle outlets. The receptacles required by this section shall be in addition to any receptacle that is:
(1) Part of a luminaire or appliance, or
(2) Controlled by a wall switch in accordance with 210.70(A)(1), Exception No. 1, or
(3) Located within cabinets or cupboards, or
(4) Located more than 1.7 m (5? ft) above the floor
A receptacle can be located 5?' above the floor and still meet the requirements of 210.52.
So theoreticaly I can place all my receptacles at 5' and still meet spacing requirements?
210.52 Dwelling Unit Receptacle Outlets.
This section provides requirements for 125-volt, 15- and 20-ampere receptacle outlets. The receptacles required by this section shall be in addition to any receptacle that is:
(1) Part of a luminaire or appliance, or
(2) Controlled by a wall switch in accordance with 210.70(A)(1), Exception No. 1, or
(3) Located within cabinets or cupboards, or
(4) Located more than 1.7 m (5? ft) above the floor
I know this is just a clarification question, and a stretch!
Is this only for a private residence? If other you might call the AHJ and ask what they say with respects to the ADA! Even future sell ablity might come into play. Somepeople total hate looking at a receptacle!
Frankly I like mine higher like 20" inches, I can only see it raising higher as we age, 14" is just low anymore...