We are doing a project and installing 400? of 300 mcm (voltage drop due to distance) fused at 150 amps at main gear and installing 200 amp rated panel board at other end. The engineer specified #6 ground wire to be installed in the same 3? conduit as the phase conductors. We asked him if the ground conductor should be larger per 250-122 Size of equipment grounding conductors- (B) ?Increased in size? when phase conductors are increased in size, (250-122(B)). The response was that it will work fine, no, do not increase the equipment grounding conductor. I have called the electrical inspector and anticipate his return call sometime late tomorrow. Is the electrical panel grounding conductor supposed to be increased in size proportionately according to the circular mil area of the ungrounded conductors? If so, how would one go about calculating that? Would it be deriving a percentage relationship between the 250-122 table of 3/0 circular mil ungrounded conductors to the #6 required grounding conductor size and then take that percentage and apply it to the 300 mcm and then look up the circular mil in the tables and choose the conductor that has that minimum value or would one assume the 300mcm for 285 amps if fused to rating and then look up table 250-122 and determine the proper size which would be a #4 conductor?
Thank you
Thank you