Dairy called & said one of his 480v pumps would run but the other would click on off on off every second or two & now wouldn't run at all. Nice SQD overload relay contacts were stuck open. Okay, jumper the overload do a quick hand operation and you can hear the overlaods click click click. Amp check showed horrible imbalance of current. Voltage check showed 315, 250 and 315 to ground. Checked other motor and imbalance was there as well but it did not have the fancy overloads to detect the imbalance.
Problem was POCOs with some line regulators and related substation troubles the night before. There are two services to this dairy fed from the same primary. One is 3 ph 240 hi leg. The other is 480/277 with a 240/120 single phase derived from it. The only problem was with the 480v motors. The single phase fans derived from the 480v step down were just fine. The 240v 3phase service voltage was good and all the motors on it were working.
Can some one shed some light as to why only the 480 had problems & not anything else.
Problem was POCOs with some line regulators and related substation troubles the night before. There are two services to this dairy fed from the same primary. One is 3 ph 240 hi leg. The other is 480/277 with a 240/120 single phase derived from it. The only problem was with the 480v motors. The single phase fans derived from the 480v step down were just fine. The 240v 3phase service voltage was good and all the motors on it were working.
Can some one shed some light as to why only the 480 had problems & not anything else.