stray voltage

Status
Not open for further replies.

j rae

Senior Member
I have a set of 150 watt H.P.S. street lights. One of my aluminum poles is reading 85 volts to ground. I have disconected the head and drove a ground rod still have the voltage. Any ideas ??????
 

mcclary's electrical

Senior Member
Location
VA
How are you measuring this? and with what? I doubt you have, what you think you have. If it's TRULY voltage on the pole, driving a rod will not fix it. You need a low resistance path back to service. Is there an EGC?
 

j rae

Senior Member
How are you measuring this? and with what? I doubt you have, what you think you have. If it's TRULY voltage on the pole, driving a rod will not fix it. You need a low resistance path back to service. Is there an EGC?
I am useing a Fluke meter from pole to ground and I was shocked by the voltage.
 

mcclary's electrical

Senior Member
Location
VA
That's probably a high impedence meter that is measuring the dfference in these two points,,,but,,If you were shocked, there's no denying that. You have a fault in the light or in the wiring. There is a problem with your EGC getting this fault back to the service. String a groung to service and measure with a wiggy from pole to the KNOWN GROUND.
 
Last edited:

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
I am useing a Fluke meter from pole to ground and I was shocked by the voltage.
... in more ways than one. ;)

Remember, voltage is a difference between points. The question is which one has the voltage above earth.

Either the EGC is energized, or there's a fault to what should be bonded, possibly inside the fixture itself.
 

hardworkingstiff

Senior Member
Location
Wilmington, NC
I have a set of 150 watt H.P.S. street lights. One of my aluminum poles is reading 85 volts to ground. I have disconected the head and drove a ground rod still have the voltage. Any ideas ??????

Is the EGC connected to the pole when you take this reading?

Where are you getting your ground reference?

Are you able to cut only the light pole circuit off and then take the reading again? Just to be sure it's coming from the light circuit and not an outside source.
 