EdwardSWard
Member
I'm aware of article 250.122(F) that "full sized" EGC's are required in each raceway where phase conductors are run in parallel in different raceways.
Question 1: Can anyony explain why?. Insulated EGC's will be the same length as they're terminated at the same points on each end. Thus, won't they each carry the same amount of fault current? Isn't it the phase conductors that will carry different amounts of fault curent depending on the location of the fault?
Question 2: Article 215.2(A)(1) states: "The size of the feeder circuit grounded conductor shall not be smaller than that required by 250.122, except that 250.122(F) shall not apply where grounded conductors are run in parallel".
Is there a typo in this article's usage of "grounded" instead of "grounding"? If so, just for the first "grounded" but not the second? (i.e. 250.122(F) doesn't apply if the feeder has parallel neutrals?)
Question 1: Can anyony explain why?. Insulated EGC's will be the same length as they're terminated at the same points on each end. Thus, won't they each carry the same amount of fault current? Isn't it the phase conductors that will carry different amounts of fault curent depending on the location of the fault?
Question 2: Article 215.2(A)(1) states: "The size of the feeder circuit grounded conductor shall not be smaller than that required by 250.122, except that 250.122(F) shall not apply where grounded conductors are run in parallel".
Is there a typo in this article's usage of "grounded" instead of "grounding"? If so, just for the first "grounded" but not the second? (i.e. 250.122(F) doesn't apply if the feeder has parallel neutrals?)