I have a project with electrical services for a multi-tenant building. Each tenant's space is separately metered with a main breaker (200A at 208 volt, 3 phase) service disconnect and meter located on a retaining wall (approximately 50 feet from the building) near the power company's transformer. Each service then feeds a tenant panel with main breaker within each tenant space. The neutral and ground are bonded together at each service disconnect with #4 ground from this point to a common grounding electrode system for all the tenant's services using #3/0.
The local inspector is viewing the retaining wall as a separate structure and stating (per 250.32) that the grounding system must generate from the tenant panels as well as a ground at the service disconnects. This seems to be in violation of 250.24(A)(5). Although the definition is vague in Article 100 for a Structure, it seems that if there are no power utilization items at the retaining wall then it should not be defined as a separate structure or building.
The local inspector is viewing the retaining wall as a separate structure and stating (per 250.32) that the grounding system must generate from the tenant panels as well as a ground at the service disconnects. This seems to be in violation of 250.24(A)(5). Although the definition is vague in Article 100 for a Structure, it seems that if there are no power utilization items at the retaining wall then it should not be defined as a separate structure or building.