electricmanscott
- Boston, MA
Well, as a matter of fact it is, we just don't know when.
Roger
Oh yes we do. 2012 Plan accordingly.
Roger
This is the biggest incorrect meme about the issue. An Outlet is current, only, passing a point . . . current taken by utilization equipment somewhere in the circuit of the current. A Receptacle doesn't utilize anything either.Because the Code is silent about "Switch Outlet" doesn't prove the negative that there is no Switch Outlet.
But I'll take my four Code citations (Post #21) over your Code silence.
I didn't write the four Code citations I note. I merely saw how they interlink.So Article 220 will now account for snap switches? ??VA each
Nope, the fact is that there is no such thing as a "switch outlet" and the majority agree :grin:
Roger
The Lemming believes in majority rule.
This is the defimition "A point on the wiring system at which current is taken to supply utilization equipment. " Simple english with no spin. A switch is just what this describes.
Yes the "point" can effectively be anywhere on the Premises Wiring (System), but not anywhere on the "circuit", as the circuit includes the source side of the Service Point (Art. 100) and the "downstream" side of the Outlet, i.e., the Utilization Equipment and its associated wiring.But it does not say that 'a point' must be a device. It can be ANY point on the premise wiring. It can be a point anywhere on the branch circuit conductor. The breaker. The bus bar. A splice anywhere in the circuit.
The bus side of the AFCI is not a 15 or 20 A 125 V circuit, the bus is protected by the OCPD ahead of the AFCI breaker.So how do you AFCI-protect the breaker itself and it's connection with the bus-bar?
While the Code "does not say that 'a point' must be a device", it doesn't exclude devices. An Outlet most certainly occurs inside a receptacle device. And, thinking of non-device outlets, I immediately think of a built in oven with a factory supplied flex whip that is wire nutted to the branch circuit conductors . . . there the wire nuts hold the Outlet.
The AFCI breaker is identified for switching duty, I think. . . I actually haven't verified this yet. . . I know virtually all 15 and 20 A commodity single pole breakers are identified SWD, that is, as switches. Say the AFCI breaker is identified for switching duty and, therefore, an outlet occurs in the switch used as a controller. . . looking at the turn of phrase in 210.12(B), I ask, does the AFCI breaker supply the outlet inside the breaker. I think not. The AFCI definitely supplies the outlets out on the branch circuit, just not the outlet that occurs in itself.
In the strictest sense, the Outlet in a switch occurs at the point between the line side of the switch and the wiring internal to the switch. The line side of an AFCI breaker is not a 15 or 20 A 125 V circuit, therefore, the Outlet occuring in an AFCI breaker doesn't fall under 210.12(B).
Yes. And the breaker, if a switch, IMO, has an Outlet in it.Is not the connection between the bus bar and the breaker 'a point on the wiring system at which current is taken to supply utilization equipment'?
Sure, the terminals are a point on the Premises Wiring (System). What's missing is that one side or the other, of the point, has to be not part of the Premises Wiring (System) - Article 100.Would not the terminals on the main be considered as 'a point....."?
Which lugs? Line or load? Is the Service Point at the line lugs? If so, see the next response. If there is no Service Point, see my previous response, directly above.Or the lugs in the meter socket?
That's an interesting question. Again, is this the Service Point, or is it a connection at a weatherhead for the overhead feeder to, let's say, my dwelling associated detached garage? The Service Point is defined as such, that is, a Service Point. Kinda looks like an Outlet, with Premises Wiring (System) on one side and "not" Premises Wiring (System) on the other side. The difference, seems to me, is the current is supplied at the Service Point, not taken.Or the connections at the weatherhead?
.......What's missing is that one side or the other, of the point, has to be not part of the Premises Wiring (System) - Article 100........
Premises Wiring (System). Interior and exterior wiring, including power, lighting, control, and signal circuit wiring together with all their associated hardware, fittings, and wiring devices, both permanently and temporarily installed. This includes (a) wiring from the service point or power source to the outlets or (b) wiring from and including the power source to the outlets where there is no service point.
In all but rare cases, modern wiring practice is to install a massively parallel system of Outlets. That's the basis of being able to install an Outlet anywhere along a Code approved installation.Seems to me everything from the weatherhead to the last receptacle on a branch circuit is part of the Premises Wiring (System)They way 'Outlet' is defined, 'a point' could be anywhere on 'the System'.Premises Wiring (System). Interior and exterior wiring, including power, lighting, control, and signal circuit wiring together with all their associated hardware, fittings, and wiring devices, both permanently and temporarily installed. This includes (a) wiring from the service point or power source to the outlets or (b) wiring from and including the power source to the outlets where there is no service point.
The Code is silent about whether an Outlet can be in series with an Outlet.Seems to me everything from the weatherhead to the last receptacle on a branch circuit is part of the Premises Wiring (System).
You omitted the last sentence of the Article 100 Definition:Seems to me everything from the weatherhead to the last receptacle on a branch circuit is part of the Premises Wiring (System).
Such wiring does not include wiring internal to appliances, luminaires, motors, controllers, motor control centers, and similar equipment.
Switch must be afci 2005 code I did not check 2008 yet for changes in definition.You omitted the last sentence of the Article 100 Definition:
I await with baited breath your explanation of why only the first two sentences of a three sentence definition of Premises Wiring (System) is the definition of Premises Wiring (System).Because it is irrelevent to the discussion.
So, in your mind, "controllers", in the third sentence, are Utilization Equipment?The third sentence is about that very utilization equipment.
The discussion is about an outlet. An outlet is "A point on the wiring system at which current is taken to supply utilization equipment.". What is attached to that outlet is not an outlet then. The third sentence is about that very utilization equipment. That is why it is irrelevant to the discussion.