We are submetering from an existing buildilng service. I have a contractor who has already installed a meter socket (which requires the glass meter) telling me we have to get the power company to come install the glass. The construction drawings say to install an e-mon d-mon. No call was ever made to the electrical engineer by the contractor saying he was going to make this change, but if we have to get the POCO involved it will be weeks before we can get the glass and have this cellular equipment up and running (that was the whole point of submetering with an e-mon!!). I'm trying to determine if this socket he installed was actually necessary. He's telling me that he couldn't install an e-mon d-mon. See below...
We have an existing 120/240v, 3 ph, 4 w, 800A disconnect switch in the existing building. It feeds a wireway, and we designed the construction drawings for tapping the conductors in the wireway, putting in a 200A/2P fused disconnect, and then a j-box wth current transformers for an e-mon d-mon. The contractor is telling me because they had to crimp onto the feeder, they had to put in a meter socket and thus, he needs the POCO to come install the meter into the can.
My information tells me this is a house switch, not a POCO switch. Why does tapping the feeder make it impossible to use an e-mon d-mon for a submeter here? I would have thought that ONLY if this was a POCO 800A switch would we need a socket rather than an e-mon. Is there something physical about tapping the feeder that requires a socket rather than using the current transformers for an e-mon? (This is in VA, Fairfax Co.)
Thanks!!
We have an existing 120/240v, 3 ph, 4 w, 800A disconnect switch in the existing building. It feeds a wireway, and we designed the construction drawings for tapping the conductors in the wireway, putting in a 200A/2P fused disconnect, and then a j-box wth current transformers for an e-mon d-mon. The contractor is telling me because they had to crimp onto the feeder, they had to put in a meter socket and thus, he needs the POCO to come install the meter into the can.
My information tells me this is a house switch, not a POCO switch. Why does tapping the feeder make it impossible to use an e-mon d-mon for a submeter here? I would have thought that ONLY if this was a POCO 800A switch would we need a socket rather than an e-mon. Is there something physical about tapping the feeder that requires a socket rather than using the current transformers for an e-mon? (This is in VA, Fairfax Co.)
Thanks!!