Close, but it's just 6 feet. You are confusing the requirement for space directly above the panel with the height of the working space in front of the panel.. . . 6-1/2 feet up from the top of the panel . . . .
Yes, see 110.26(F)(1)(c).Can you mount a sprinkler head inside an electrical room?