Water Piping Clearances for Panels, etc

Status
Not open for further replies.

rbeery

Member
Our there any specific clearances for water piping around electrical equipment. Is it ok for electrical panels to be located in the same room as fire suppression water piping?
 

DARUSA

Senior Member
Location
New York City
110.26 F 1 a Dedicated equipment space

110.26 F 1 a Dedicated equipment space

Deep of the panel and 6-1/2 feets up from the top of the panel or to the celing whatever is first.
 

charlie b

Moderator
Staff member
Location
Lockport, IL
Occupation
Retired Electrical Engineer
. . . 6-1/2 feet up from the top of the panel . . . .
Close, but it's just 6 feet. You are confusing the requirement for space directly above the panel with the height of the working space in front of the panel.

 