We have schematic/narrative design that includes feeders for pairs of
300A, 200,000 CFM fans exhausting a transit tunnel.
I'm not an engineer.
Ugly's Electrical References (book) suggests that 3/350kcmil conductors might be adequate to feed one fan, and further that these will fit in ONE 4" RGS conduit.
The engineer reviewing the estimate came back with THREE 4" conduits and
an unspecified quantity of 600 kcmil conductors, PER FAN.
It appears the feeder run is 2,200 feet so quite a lot of derating applies.
Controls wiring and conduit is separately accounted for.
How does one get from one, to three, conduits?
Is there a derating for grouped cables that leads to pulling one single conductor per conduit? Even in that case, the conduit size would be far smaller.... the Transit Agency uses an EPR insulated cable that is nothing unusual sofar as diameter.
300A, 200,000 CFM fans exhausting a transit tunnel.
I'm not an engineer.
Ugly's Electrical References (book) suggests that 3/350kcmil conductors might be adequate to feed one fan, and further that these will fit in ONE 4" RGS conduit.
The engineer reviewing the estimate came back with THREE 4" conduits and
an unspecified quantity of 600 kcmil conductors, PER FAN.
It appears the feeder run is 2,200 feet so quite a lot of derating applies.
Controls wiring and conduit is separately accounted for.
How does one get from one, to three, conduits?
Is there a derating for grouped cables that leads to pulling one single conductor per conduit? Even in that case, the conduit size would be far smaller.... the Transit Agency uses an EPR insulated cable that is nothing unusual sofar as diameter.