Section 110.14(C)(1) states that where conductors are terminated in equipment, the selected conductor ampacities must be based on Table 310.16, unless the equipment is specifically listed and marked otherwise. The intent of this requirement is to clarify which ampacities are used to determine the proper conductor size at equipment terminations.
When equipment of 600 volts or less is evaluated relative to the appropriate temperature characteristics of the terminations, conductors sized according to Table 310.16 are required to be used. The UL General Information Directory (White Book) clearly indicates that the 60?C and 75?C provisions for equipment have been determined using conductors from Table 310.16. However, installers or designers unaware of the UL guide card information might attempt to select conductors based on a table other than Table 310.16, especially if a wiring method that allows the use of ampacities such as those in Table 310.17 is used. That use can result in overheated terminations at the equipment. Clearly, the ampacities shown in other tables (such as Table 310.17) could be used for various conditions to which the wiring method is subject (ambient, ampacity correction, etc.), but the conductor size at the termination must be based on ampacities from Table 310.16. This change does not introduce any new impact on the equipment or the wiring methods; it simply adds a rule from the listing information into the Code because it is an installation and equipment selection issue.