I attended Mr. Holt's Florida EC licensing program circa 1983. Am and have been registered PE since, State EC license 614, inactive since 1986.
Situation- Landfill has Methane recovery serving 2- 500KW M/G sets, secondary voltage 4160. Oil pump failed, causing total burnout. Replacement is under way. All wiring within covered steel building is Nema 1, combination of RGC and EMT, some PVC, all Nema 1 devices.
Reading NEC 500, it identifies Methane as Class I Div II Group D. I don't see this as a hazardous area, but can't find a way to substantiate it. 500/501/502 don't leave any 'outs' for airflow, ventilation, or exposure.
Methane is .6 specific gravity, so putting outlets low is a good thing, but do they need to be installed and wired to Class I standards? Also, lighting within that cavity needs to be replaced, Existing facility has been operating since 1996 with no electrical issues.
Your thoughts, please. Giles Electric is my client in this case.
Thanks,
Paul Estes, P.E.
Situation- Landfill has Methane recovery serving 2- 500KW M/G sets, secondary voltage 4160. Oil pump failed, causing total burnout. Replacement is under way. All wiring within covered steel building is Nema 1, combination of RGC and EMT, some PVC, all Nema 1 devices.
Reading NEC 500, it identifies Methane as Class I Div II Group D. I don't see this as a hazardous area, but can't find a way to substantiate it. 500/501/502 don't leave any 'outs' for airflow, ventilation, or exposure.
Methane is .6 specific gravity, so putting outlets low is a good thing, but do they need to be installed and wired to Class I standards? Also, lighting within that cavity needs to be replaced, Existing facility has been operating since 1996 with no electrical issues.
Your thoughts, please. Giles Electric is my client in this case.
Thanks,
Paul Estes, P.E.