15 amp devices on 20 amp ctkt

Status
Not open for further replies.

stevej

Member
Can you install a 15 amp recpt on #12 wire on a 20 amp breaker?? Would like code ref if yes.
thanks,
Steve
 

njatc

Member
Yes you can as long as it is not a dedicated circuit.It says in article 210.21(B)
(1) that a single recepticle (not duplex) installed on an individual branch circuit shall have an ampere rating not less than that of the branch circuit.Basically if you are installing a dedicated circuit to a recepticle, that recepticle has to be a single recepticle equal to the branch circuit rating, but if you are installing two or more 15 amp duplex recepticles then they can be on a 20 amp circuit.
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
.................. but if you are installing two or more 15 amp duplex recepticles then they can be on a 20 amp circuit.

I believe if you look at the definitions of a receptacle in references and note "contact device", you will find it permissible to install a (one) 15 amp DUPLEX on a 20 amp circuit.
 