Splicing ground wire to the water line.

Status
Not open for further replies.

lakee911

Senior Member
Location
Columbus, OH
Is it permissible to splice the GEC from the service disconnect to the water supply line? Furthermore, does it matter where the GEC attaches to the water supply line provided that there is a bonding jumper accoss the meter?

I do understand that the GEC to ground rod can not be spliced.

Thanks
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
Is it permissible to splice the GEC from the service disconnect to the water supply line?
Yes, if done properly 250.62(C)
Furthermore, does it matter where the GEC attaches to the water supply line provided that there is a bonding jumper accoss the meter?
The way I read it, yes. 250.52(A)(1) states that beyond 5 ft the line shall not be used as a grounding electrode conductor.
I do understand that the GEC to ground rod can not be spliced.

Thanks
misunderstand...see 250.62(C) again
 

gndrod

Senior Member
Location
Ca and Wa
Yes, if done properly 250.62(C)

The way I read it, yes. 250.52(A)(1) states that beyond 5 ft the line shall not be used as a grounding electrode conductor.

misunderstand...see 250.62(C) again

Gus, Sorry to interrupt, but did you mean [250.64(C)]? rbj
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
interruptions welcomed.... eyeglasses more welcomed.... thanks View attachment 3855
250.64
(some times I fail to see the top of the page evidently)
 