Current sense as you are using it is embedded in the physics of the event. Ohms Law still applies. What if the load were removed from the circuit? Wouldn't the voltage still be present and measurable. Current is zero, right? What if you removed the node (i.e. opened all pathways at the node)? Wouldn't the voltage still be present across the conductor ends? Again, current is zero, right?You still have a current sense. You are using the voltage polarity & power factor to derive the current sense. :roll:
My point remains that I do not have to adopt the positive-negative convention to obtain through calculation the unknown current "In". That is to say, in resolving the problem I do not have to assign a plus (+) symbol to a known current entering a node or assign a minus (?) symbol to that known current if it is "not entering" that node, or vice-versa with respect to leaving or not leaving. The phase angles takes care of that, and phase angles can be determined through parameters other than current. So no assigning of a positve or negative to a current value is necessary. Since you believe I am, can you tell me exactly where am I assigning a positive or negative (symbol) to a current variable?
The only way I can even phathom that you got your stated results is if you used forward rotation and flopped values. When you use reversed rotation, phasors rotate clockwise, same as when you flop any two lines on a 3? motor.Using In+Ia+Ib+Ic=0, we sum the currents and multiply by -1 and In would be 6.07A with an angle of 26.4?
Using In=Ia+Ib+Ic, we sum the currents and In would be 6.07A with an angle of 206.4?
Below, yes.That is my preference as well and what I used.
Above...
And in the latter of the two above, we are back to the equation that started all of this.Using In+Ia+Ib+Ic=0, we sum the [known] currents and multiply by -1 and In would be 11.62A with an angle of 315.6?
Using In=Ia+Ib+Ic, we sum the currents and In would be 11.62A with an angle of 135.6?
The latter equation should be ?In=Ia+Ib+Ic.
You can verify this by plotting out the vectors in an arrow to tail progression.