DataCenterGuy
Member
- Location
- New York
Article 645.5(E) "Securing in Place" (any version since 1993) states "Power cables, . . . connectors, plugs, and receptacles . . . for information technology equipment shall NOT be required to be secured in place." (Emphasis added.)
I have had AHJ's pass under-floor (air plenum) installations that ARE secured in place and are NOT Article 645 compliant (No EPO). But we can't identify Code that authorizes this.
Does anyone know if anywhere in the Code specifically allows Wireways and Receptacles to be secured in place under an air plenum raised floor in a room with no EPO Switch and still allow under-floor plug-in. (I realize that this can be jurisdiction-specific, but am interested for now in the NEC - any version.)
I have had AHJ's pass under-floor (air plenum) installations that ARE secured in place and are NOT Article 645 compliant (No EPO). But we can't identify Code that authorizes this.
Does anyone know if anywhere in the Code specifically allows Wireways and Receptacles to be secured in place under an air plenum raised floor in a room with no EPO Switch and still allow under-floor plug-in. (I realize that this can be jurisdiction-specific, but am interested for now in the NEC - any version.)