the code states emt shall be permitted as a equipment grounding conductor. ive just heard this and read this. does anything alter this and does anyone do this? and can inspectors fail this?
Correctthe code states emt shall be permitted as a equipment grounding conductor.
No. In Art 517 it must be augmentedive just heard this and read this. does anything alter this?
a number of folks... search here and you will find where it can be a better ground than a conductorand does anyone do this? ?
not legitimatelyand can inspectors fail this?
the code states emt shall be permitted as a equipment grounding conductor. ive just heard this and read this. does anything alter this and does anyone do this? and can inspectors fail this?
i just feel its better to have the ground than not.
ok my question is what happens if something down th rode happens to the pipe u could loose the ground? and sorry for asking but why is it a better ground and do you use regular emt fittings or special ones, really curious on this cause ive never come across it
ok i get that but im talking about running emt for lights and outlets and u dnt run an ground wire, and how would u properly size emt as an egc?
Patsy, you might want to take a peek at this,.. short sweet and informative
http://www.nema.org/stds/eng-bullet...ConduitandEMT-ProventoMeettheNECReg_03_09.pdf
... RSC, IMC and EMT are all permitted as an equipment grounding conductor in accordance with NEC? 250.118. It is permitted to add a supplementary equipment grounding conductor sized in accordance with NEC? 250.122. This is a systems design consideration. If a supplementary equipment grounding conductor is used, it is still very important to comply with NEC? 300.10 and 300.12, since approximately 90% to 95% of the current will flow on the conduit and not in a supplementary conductor. For information on the equipment grounding capabilities of RSC, IMC and EMT, click here for a link to the section with the results of a research study performed by the Georgia Institute of Technology.
hey cpal i just read it and ive got to say ive never heard that about using the emt as the ground i just dnt no how my area inspectors would feel about it ilike to thank u all for the info uve given me?
hey cpal i just read it and ive got to say ive never heard that about using the emt as the ground i just dnt no how my area inspectors would feel about it ilike to thank u all for the info uve given me?
I don't ever remember a time when it couldn't be used, outside of specs calling for an EGC anyway, and I've been wiring for a long time.hey cpal i just read it and ive got to say ive never heard that about using the emt as the ground i just dnt no how my area inspectors would feel about it ilike to thank u all for the info uve given me?