Dwelling Unit Bedroom

Status
Not open for further replies.

flashlight

Senior Member
Location
NY, NY
Occupation
Electrician, semi-retired
We are the electrical subcontractors for the remodel of a studio apartment of 400 sq. ft., consisting of one large L-shaped room, and a separate kitchen and bathroom. The bed is in one "leg" of the L, the other leg comprises the living/dining room. For the purposes of 210.12 (B) is the entire open room considered the dwelling unit bedroom, therefore requiring all receptacles to be AFCI protected ?
 

flashlight

Senior Member
Location
NY, NY
Occupation
Electrician, semi-retired
I should mention that we are on the 2005 cycle.
But I guess we should just pretend we are on the 2008 and make
them all AFCIs, to remove all doubt ?
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
Flash, I'd consider them to be separate rooms. The same situation arises in great rooms and kicthen/dining areas.

If you could draw a dotted line on the plans denoting areas, you can use those lines to separate rooms without walls.
 

raider1

Senior Member
Staff member
Location
Logan, Utah
Only the AHJ in your area can really determine the extent of the bedroom area.

I would recommend contacting the local building department.