Is it permissable to connect to a dryer circuit in the outlet box and feed a water heater so long as the OCP is okay? I have researched this and cannot find anything that says that a dryer must be on an individual branch circuit.
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
assuming you have no means to keep them from operating simultaneously, from the water heater standpoint, a single overcurrent device big enough to supply both would be a violation of 210.23 and 422.11(E).
 