You put one-half 1? line-to-line load's kVA in panel schedule columns.I am still a bit comfused, in my question i get 8 amps i think that is wrong and then do i put 8 [or the correct answer ]in column A and B [or whatever 2 phases i use]
3664 divided by 480 is about 7.6, so 8 is a close enough answer.. . . in my question I get 8 amps (I think that is wrong). . . .
No. That is my earlier point. You don't put amps into any column. Never try to add amps to amps. It very seldom gives you the right answer.. . . and then do i put 8 . . . in column A and B. . . .
Where does 1.83 come from?You put one-half 1? line-to-line load's kVA in panel schedule columns.
In your case of a 3,664W heater, VA equals watts. Converted to kVA would be 3.664kVA... So you put 1.83 in each of the two columns a load is connected to... or multiples thereof if connecting more than one heater per circuit.
It is half of 3.66. For a single phase, 480 volt load that is connected between phases A and B, for example, half of the KVA load should be assigned to phase A, and the other half to phase B.Where does 1.83 come from?
Got it. thanks. I was working the problem out in VA and not KVA and missed his decimal point.It is half of 3.66. For a single phase, 480 volt load that is connected between phases A and B, for example, half of the KVA load should be assigned to phase A, and the other half to phase B.