When installing a panelboard on a secondary I have always put in a main breaker.
I have a customer ask me to add some circuits to a panel and noticed no main breaker feeding a 200A 42 circuit Main Lug panelboard 120/208 from a 75KVA 480x120/208 transformer and there is a 90A breaker on the primary side. I did a little investigating and it is ok if it is 6 circuits or less. With a 42 circuit panelboard though a Main breaker would be required. Am i right?
Exhibit 450.4 and Exhibit 450.5 are what I was using for reference.
I have a customer ask me to add some circuits to a panel and noticed no main breaker feeding a 200A 42 circuit Main Lug panelboard 120/208 from a 75KVA 480x120/208 transformer and there is a 90A breaker on the primary side. I did a little investigating and it is ok if it is 6 circuits or less. With a 42 circuit panelboard though a Main breaker would be required. Am i right?
Exhibit 450.4 and Exhibit 450.5 are what I was using for reference.