5-254 Log #3527 NEC-P05 Final Action: Accept in Principle in Part
(250.104(C))
_______________________________________________________________
Submitter: Phil Simmons, Olympia, WA
Recommendation: Revise the existing text of the 2008 NEC as follows:
(C) Structural Metal. Exposed structural metal that is interconnected to form
a metal building frame and is not intentionally grounded or bonded and is
likely to become energized shall be bonded to the service equipment enclosure,
the grounded conductor at the service, the grounding electrode conductor if
where of sufficient size, or the one or more grounding electrodes used. The
bonding jumper(s) shall be sized in accordance with Table 250.66 except as
permitted in 250.104(A)(2) and (A)(3) and installed in accordance with
250.64(A), (B), and (E). The points of attachment of the bonding jumper(s)
shall be accessible unless installed in compliance with 250.68 Exception No. 2.
Substantiation: The phrase ?likely to become energized? is proposed for
deletion as most often, electrical inspectors enforce bonding of structural metal
if the building or structure has exposed metal members and the building or
structure is supplied with a service, feeder or branch circuit.
The reference to 250.104(A)(2) and (A)(3) will allow adjustment in the size
of bonding conductors and jumpers if the building s supplied by a feeder.
The reference to 250.68 Exception No. 2 permits the connection of bonding
conductors or jumpers to be fireproofed and not be accessible if appropriate.
Section 3.3.4 of the NEC Style Manual states that ?where? should not be used
to mean ?when? or ?if.? This proposal intends to use the word ?if? where
appropriate.
Panel Meeting Action: Accept in Principle in Part
Revise text to read as follows:
the grounded conductor at the service, the disconnecting means for buildings or
structures supplied by a feeder or branch circuit, the grounding electrode
conductor where if of sufficient size, or the one or more grounding electrodes
used.
The bonding jumper(s) shall be sized in accordance with Table 250.66
and installed in accordance with 250.64(A), (B), and (E). The points of
attachment of the bonding jumper(s) shall be accessible unless installed in
compliance with 250.68(A) Exception No. 2.
Panel Statement:
The panel does not accept the deletion of ?likely to become energized?. If the AHJ believes the structural metal is likely to become
energized then bonding is required. There is no reason to eliminate the
flexibility provided when situations occur involving structural metal that is
unlikely to become energized. The panel does not accept the recommendation
to refer to Sections 250.104(A)(2) and (A)(3) because these sections cover
bonding of metal water piping. The panel action on Proposal 5-253 has been
incorporated into the panel action on this proposal.
Number Eligible to Vote: 16
Ballot Results: Affirmative: 16